Non-Corrosive and/or Dielectric Liquid Cooling?

This forum is for specialized infomation important to the construction and safe operation of the high voltage electrical supplies and related circuitry needed for fusor operation.
ian_krase
Posts: 553
Joined: Mon Nov 28, 2016 7:48 am
Real name: Ian Krase

Non-Corrosive and/or Dielectric Liquid Cooling?

Post by ian_krase » Sat Oct 12, 2019 5:28 am

If you're like me, then in the course of vacuum work you come across the fact that glow discharges and particle beams easily heat things up... too hot. Hot enough to demagnetise, to outgas or oxidize, to melt, to enter thermionic runaway, or to destroy plastics or rubber seals.

The solution of course is liquid cooling. But this has some problems. As every liquid-cooled gaming PC afficionado knows, mixing copper and aluminum in the same system, even if they are not electrically connected, is just asking for a mess of galvanic corrosion that will pit and pinhole the aluminum pretty rapidly. And this applies more generally.

Also, if you're using water with additives for coolant, you can't have something you're cooling at other than ground potential. The coolant will conduct.


The solution to this is to use dielectric coolant, and that has... problems.

The best-known dielectric coolants seem to be "Fluorinert" and various other fluorocarbon or PFPE-based liquids. These are expensive and probably not great for the enviroment or health. Most ordinary hydrocarbons are far too flammable, as well as being polluters if they evaporate and tending to destroy plastics.


What are my options?

Andrew Seltzman
Posts: 720
Joined: Mon Feb 02, 2004 1:02 am
Real name: Andrew Seltzman
Contact:

Re: Non-Corrosive and/or Dielectric Liquid Cooling?

Post by Andrew Seltzman » Sat Oct 12, 2019 6:51 pm

Fluorinert is best. It has no health issues at all, unless you burn it (don't).

https://www.ebay.com/itm/3M-Fluorinert- ... SwpOVdhGs6
https://www.ebay.com/itm/3M-Fluorinert- ... SwsR9c73pt
Andrew Seltzman
www.rtftechnologies.org

User avatar
Richard Hull
Moderator
Posts: 11467
Joined: Fri Jun 15, 2001 1:44 pm
Real name: Richard Hull

Re: Non-Corrosive and/or Dielectric Liquid Cooling?

Post by Richard Hull » Sat Oct 12, 2019 7:56 pm

The idea of cooling in the fusor goes way back on this site. From cooling a grid made of hypo needle tubing with flowing coolant, to cooling the fusor body when Carl Willis brazed1/4" copper piping to his hemispheres and pumped ice water through them.

Cooling the grid seems the most difficult. Cooling the chamber walls might just assist in allowing more D2 wall loading. General plasma streamlines require steering gear or potential shielding screens over sensitive regions where such beams might hit sensitive items which might out-gas or be damaged within the vacuum chamber, itself. As noted, cooling within a vacuum and among HV components within can be daunting.

Fluorinert has been mentioned many times here.

Richard Hull
Progress may have been a good thing once, but it just went on too long. - Yogi Berra
Fusion is the energy of the future....and it always will be
Retired now...Doing only what I want and not what I should...every day is a saturday.

ian_krase
Posts: 553
Joined: Mon Nov 28, 2016 7:48 am
Real name: Ian Krase

Re: Non-Corrosive and/or Dielectric Liquid Cooling?

Post by ian_krase » Sun Oct 13, 2019 12:18 am

Interesting.

Flouorinert has a fairly low vapor pressure. Do you need to make a completely closed system?

User avatar
Bob Reite
Posts: 340
Joined: Mon Aug 26, 2013 1:03 am
Real name: Bob Reite
Location: Wilkes Barre/Scranton area

Re: Non-Corrosive and/or Dielectric Liquid Cooling?

Post by Bob Reite » Sun Oct 13, 2019 1:53 am

My vacuum chamber does have a water jacket (or liquid jacket if you prefer) I never got around to hooking it up yet. I believe there are some archived posts here with someone cooling the grid with Flouorinert. Because of the expense, the Flouroinert loop goes to a water cooled heat exchanger close to the grid feedthrough.
The more reactive the materials, the more spectacular the failures.
The testing isn't over until the prototype is destroyed.

John Futter
Posts: 1446
Joined: Thu Apr 22, 2004 2:29 am
Real name: John Futter
Contact:

Re: Non-Corrosive and/or Dielectric Liquid Cooling?

Post by John Futter » Sun Oct 13, 2019 4:21 am

Professional systems like accellerator mass spectrometers use deodorised kerosine to cool the ion source
I use ordinary kerosine to cool my ion sources at work ie 500 - 1500 watts of heat input tends to destroy the ion source magnets if the cooling stops.
Kero runs closed loop into a heat exchanger that is water cooled. Ion source has a copper backing plate that the kero flows through
and I use a petrol pump as used at service stations to circulate but you could use a high flow rate car type fuel pump


Cheap as chips

ian_krase
Posts: 553
Joined: Mon Nov 28, 2016 7:48 am
Real name: Ian Krase

Re: Non-Corrosive and/or Dielectric Liquid Cooling?

Post by ian_krase » Sun Oct 13, 2019 5:28 am

By "completely closed system" I mean one that's all sealed up, not just a closed loop.

Andrew Seltzman
Posts: 720
Joined: Mon Feb 02, 2004 1:02 am
Real name: Andrew Seltzman
Contact:

Re: Non-Corrosive and/or Dielectric Liquid Cooling?

Post by Andrew Seltzman » Sun Oct 13, 2019 5:43 am

Here is the documentation on the fluorinert cooling of my grid:
http://www.rtftechnologies.org/physics/ ... -index.htm

Fluorinert does evaporate slowly (much slower than ethanol), so a mostly closed system is recommended. A simple plastic cap or over pressure vent valve on the reservoir will do. It doesn't have to be a hermetic seal, but it shouldn't be an open reservoir either.
Andrew Seltzman
www.rtftechnologies.org

Dan Knapp
Posts: 280
Joined: Wed Aug 06, 2008 12:34 pm
Real name: Dan Knapp

Re: Non-Corrosive and/or Dielectric Liquid Cooling?

Post by Dan Knapp » Sun Oct 13, 2019 11:24 am

Behlke (Behlke.com) uses a sealed closed loop fluorinated fluid system to cool and insulate their HV pulse switches. They use a pump which is sold for cooling computer CPU’s. There are a large number of different pumps sold for this purpose largely to the high performance gaming community. This would be a source of reasonably priced cooling components.

User avatar
Rich Feldman
Posts: 1130
Joined: Mon Dec 21, 2009 11:59 pm
Real name: Rich Feldman
Location: Santa Clara County, CA, USA

Re: Non-Corrosive and/or Dielectric Liquid Cooling?

Post by Rich Feldman » Sun Oct 13, 2019 7:14 pm

Two angles here.
1) Water is used as a HV dielectric in some pulse forming networks, where its high dielectric constant is favorable for electrode geometry reasons.
But even if deionized to double-digit resistivity (in megohm-cm), which is hard to keep that way, the self-discharge time of a water capacitor is on the order of a millisecond (IIRC).
Edit: RC for 1 meter cube is (8.85 X 80.1 = 709) pF X 0.18 megohm = 128 us (at 20 degrees C). The bottom line value is the same for any geometry.

2) How about long, thin tubing to make the electrical resistance tolerable in a water cooling connection? Trading off water resistivity, pressure drop, and temperature rise. Hot water is less viscous and less electrically resistive than cold. I think the electrical leakage current will galvanically eat at HV-positive pipes and not at those which are HV-negative.

I bet the main advantage of Fluorinert over refined hydrocarbons is its non-flammability.
As with PCB's in capacitors and transformers, there's an obvious & immediate benefit because it reduces the risk of fires.
As with all liquids, you need to pay attention to compatibility of wetted materials like elastomeric seals.

p.s. Regarding toxicity, ozone depletion, and global warming potential, the numbers for propane and butane are many times lower than even the latest nonflammable refrigerants.
I bet the same applies to the higher-boiling-point nonaqueous coolants under discussion in this thread.
Last edited by Rich Feldman on Mon Oct 14, 2019 12:24 am, edited 2 times in total.