FAQ - Ballasting a power transformer.

If you have a question about this topic, the answer is probably in here!
John Futter
Posts: 1582
Joined: Thu Apr 22, 2004 2:29 am
Real name: John Futter
Contact:

Re: FAQ - Ballasting a power transformer.

Post by John Futter » Mon May 26, 2014 9:19 am

Just to add

The reason a ballast is used is to add a real impedance to the circuit to limit dI/dT and dV/dT both of these terms are very destructive to all systems so limiting voltage and current transients allows control circuits to act.
As Richard and Chris have said a value somewhere between 5% and 50% of the power available is about right unless you know all the parameters of the power supply and load where you may confine these limits to a tighter range.
Taking into account response time of the supply an unballasted system will appear to have negative resistance which is the most damaging of all conditions for the supply ie this can be asking the supply to to cope with more than twice of what it is capable of.
ie the time lag of the supply tends to reinforce not negate what is happening.
The Ballast slows system response so that the supply can correct /and /or limit what is going on.
Bode plots and their theory give the insight into this--it all comes down to phase margin (a measure of lag in the power supply)


Happy Ballasting

Johannes westman
Posts: 8
Joined: Mon Apr 07, 2014 7:56 am
Real name: Johannes westman

Re: FAQ - Ballasting a power transformer.

Post by Johannes westman » Mon May 26, 2014 10:40 am

I think I need to read it again, sorry.

User avatar
Richard Hull
Moderator
Posts: 12086
Joined: Fri Jun 15, 2001 1:44 pm
Real name: Richard Hull

Re: FAQ - Ballasting a power transformer.

Post by Richard Hull » Mon May 26, 2014 1:19 pm

The key is "KNOW... and understand your supply" If you don't, you will be --ssing into the wind. No neon sign transformer based system ever needs any form of ballast. A 25 kilowatt utility pole based power supply would need a small engineering effort to properly ballast the supply, both for and aft of the transformer.

What the he-- is your supply ready to supply without bringing down the power grid or melting your fusor grid instantly? 99% of all amateur neutron club attempt fusor supplies are hard pressed to supply 30kv at 10ma. Everything in them is weak and whimpy. As noted above, for these supplies, a wire wound, 25-100 watt ceramic resistor of 30kohm to 70kv ohms will be sufficient in the hands of a good operator to prevent damage.

A dim witted, not very fast on his feet person, who never built a well instrumented demo fusor and played with it for hours is capable of destroying most any supply system. There is no ballast or supply that can survive stupidity on the part of the operator.

Intelligently applied, real watts, have to go into any successful fusor and the operator is as much a part fo the ballasting system as the physical ballasting system, itself!

Richard Hull
Progress may have been a good thing once, but it just went on too long. - Yogi Berra
Fusion is the energy of the future....and it always will be
Retired now...Doing only what I want and not what I should...every day is a saturday.

Johannes westman
Posts: 8
Joined: Mon Apr 07, 2014 7:56 am
Real name: Johannes westman

Re: FAQ - Ballasting a power transformer.

Post by Johannes westman » Mon May 26, 2014 3:13 pm

I think I know where I went wrong now. My assumption, based on insufficient knowledge about transformers was that transformers (unballasted) will simply continue to draw an ever increasing amount of current.
(My supply, btw - will be a 50kv 8ma x-ray transformer, I also have a neon transformer at 10.5 kv 30ma at hand)

Johannes westman
Posts: 8
Joined: Mon Apr 07, 2014 7:56 am
Real name: Johannes westman

Re: FAQ - Ballasting a power transformer.

Post by Johannes westman » Mon May 26, 2014 3:14 pm

I plan on running the 50kv at a lower Voltage, and a slightly higher current btw.

Post Reply