Disabling Internal GFI in newer NST?

Post by Ed Meserve »

Hi All, I need to pick your brains. The Allanson "pow R pak" NST has an internal ground fault interrupt that starts to kick in when I raise up the voltage on the variac beyond 45 VAC.
I been google-ing all over today and have had no luck finding any info on disabling GFIs. Before I dig into it, I thought I'd see what your collective thoughts were.

Thanks,
Ed
Ed Meserve
Jon Rosenstiel
Posts: 1494
Joined: Thu Jun 28, 2001 1:30 am
Real name: Jon Rosenstiel
Location: Southern California

Re: Disabling Internal GFI in newer NST?

Post by Jon Rosenstiel »

From a few years back...

viewtopic.php?f=11&t=4646#p27484

Jon Rosenstiel
User avatar
Ed Meserve
Posts: 74
Joined: Wed Oct 19, 2011 4:51 pm
Real name: Ed Meserve
Location: Maine, USA

Re: Disabling Internal GFI in newer NST?

Post by Ed Meserve »

Thanks, John! I pinged the search, but I didn't pull this up. Tough to know what to ask when you don't know what to ask. : )
Ed
Ed Meserve
David D Speck MD
Posts: 129
Joined: Sat Jan 26, 2008 2:05 pm
Real name: David D. Speck MD
Location: Auburn, NY

Re: Disabling Internal GFI in newer NST?

Post by David D Speck MD »

Ed,

First of all, is this a traditional 60 Hz iron core transformer, or a modern high frequency solid state supply? If it's a solid state high frequency supply, you are out of luck.

If it is an iron core transformer, then you may be able to remove the bottom plate and see if the GFI circuit module is identifiable. On some of the GFI protected transformers, it is a discrete unit in one corner of the case. You can trace out the wires and figure out how to bypass it.

Unfortunately, many of the modern iron core transformers are completely potted in some sort of impenetrable epoxy. Bypassing the GFIs on these is essentially impossible.

Dave Speck