Power capability question

This forum is for specialized infomation important to the construction and safe operation of the high voltage electrical supplies and related circuitry needed for fusor operation.
Post Reply
User avatar
Rich Feldman
Posts: 1470
Joined: Mon Dec 21, 2009 6:59 pm
Real name: Rich Feldman
Location: Santa Clara County, CA, USA

Re: Power capability question

Post by Rich Feldman »

For reference, here's the view when two 120V sources have phase difference of 180 degrees. Phase to phase voltage is +/- 340 V (240 V RMS), and DC bus voltage reaches 340 V as we all agree.
3phase_rect_tran4.png
Now back to the 3 phase, with load resistor now 50 ohms so average bus current is almost 6 A.
I charted the phase-to-phase voltages on both sides of phase 2, and the current pulses from phase 2 (pink) and the other 2 phases. All peaking at about 30 A in this simplistic model.
3phase_rect_tran5.png
Lower picture shows phase 3 disconnected. Capacitor-charging pulses are 3x less frequent. Each surviving phase delivers 50% more charge than before, in 2 instead of 4 pulses per cycle, with current amplitudes approximately doubled.
All models are wrong; some models are useful. -- George Box